Shared neutral with three break Breakers on three phase

reyamkram

Senior Member
Location
Hanover park, il
I have a 120 208 panel now I'm going to run convenience receptacles now I can share one neutral with all three phases is that correct or do I need to increase the neutral for the return load thank you for any and all information
 
Simply a MWBC, no need to increase the neutral size. All the scare about additive odd order harmonics has died down
 
Harmonics issues was and still is much of an issue it you have pretty intense neutral loading by non linear loads on wye systems like maybe a data center. They were more likely having more issues with service and feeder neutrals more so than the typical 20 amp "full boat" branch circuit in most cases as well. Not that the neutral wasn't seeing higher current issues but the reality also is with 240.4(D) small conductor rule the load on the conductors was more limited than for conductors over 10 AWG - A 12 AWG is rated 35 amps @ 75C, but we limit it to 20 amp circuits for most situations because of 240.4(D).

IG's were typically a result of data errors when transmitting information between items back then, most the common data transmission methods used for nearly 30 years now doesn't even have a connection to a grounded conductor or cable shield to create those same type of errors should stray currents be present on the ground or shield so isolating EGC's has no effect on the data transmission method anymore.
 