What code section is (was?) that?You are permitted to run a single neutral for multiple branch circuits but that is only permitted for outdoor lighting circuits. ...
225.7Is that 6awg on a 100A breaker? Is that breaker actually a 'service disconnect'?
What code section is (was?) that?
it is a sub panel.Is that 6awg on a 100A breaker? Is that breaker actually a 'service disconnect'?
What code section is (was?) that?
So the 100 amp breaker size may be irrelevant if the feeder is correctly protected by the upstream device.it is a sub panel.
correct. Which it is.So the 100 amp breaker size may be irrelevant if the feeder is correctly protected by the upstream device.