Where does it address this in code?
Next in a commercial job can u share
Neutrals?
Next in a commercial job can u share
Neutrals?
'Where does it address this in code?
Next in a commercial job can u share
Neutrals?
Where does it address this in code?
Next in a commercial job can u share
Neutrals?
That's an equipment issue, not a code issue.I thought the requirement was brought in more for going with the requirements for afci breakers, can't share neutrals with them, unless I'm missing something?
I thought the requirement was brought in more for going with the requirements for afci breakers, can't share neutrals with them, unless I'm missing something?
Sent from my SM-N975U using Tapatalk
Nope Have to "Simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates"I thought you only needed the handle tie if 2 circuits were on the same yoke.
It used to be that way; not, it's any MWBC.I thought you only needed the handle tie if 2 circuits were on the same yoke.
Multipole breakers yes, but handleties no, a single breaker triping with handle ties will not trip the other one or two.I never liked MWBC much. Losing a neutral means something gets burned up. When new, it does save a little time to have only the 1 neutral splice but you might start off with 4 wires to a neutral splice, then it’s harder to add a new run to a box later on.
Now a trip on 1 ckt kills other 1 or 2 as well. Hard to explain to a customer why we have to connect the breakers.
I couldn't agree more210.4(B). It goes back to 2008. I passionately hate it so much it is one of the few code references I know by heart. It's in my top two worst code changes ever. It has caused a horrible waste of resources because everyone specs dedicated neutrals now and is ruining a generation of electricians who have no understanding of a MWBC.
As with a lot of code changes, it was probably pushed by a manufacture to sell more product under the promotion that it’s safer. Which with the current new crop of electricians..........210.4(B). It goes back to 2008. I passionately hate it so much it is one of the few code references I know by heart. It's in my top two worst code changes ever. It has caused a horrible waste of resources because everyone specs dedicated neutrals now and is ruining a generation of electricians who have no understanding of a MWBC.