Sparks4All
Member
- Location
- Washington
We are doing a tenant improvement in a large building. The contractor that wired the shell ran (3)3" conduits into the space. We are installing an 800 Amp MDP in the retail space with 3 parallel runs in the 3 conduits. We will need a grounding conductor for the transformers and an isolated ground in a addition to the EGC's. There is not structural steel. The entire structure is concrete. There is no way to add a new conduit back to the GES. I don't believe we can run the grounding conductors inside one of the conduits of the parallel runs. Is this the case?