ok if its a 2 pole (or handle tied) breaker on a 120/240 3 wire system. probably not ok otherwise. see article 527.Originally posted by gent:
Temporary construction pole... two 20 amp breakers for two circuits feeding two GFCI receptacles are sharing the neutral grounded conductor.
Wrong or not?
For temporary circuits, 527.4(E) requires it.Originally posted by jap2525:
Why would you have to have handle ties? It seems there are (2) seperate gfi receptacles,they are not mounted on the same yoke.