gent

Member
Temporary construction pole... two 20 amp breakers for two circuits feeding two GFCI receptacles are sharing the neutral grounded conductor.

Wrong or not?
 
Re: Sharing a neutral

Originally posted by gent:
Temporary construction pole... two 20 amp breakers for two circuits feeding two GFCI receptacles are sharing the neutral grounded conductor.

Wrong or not?
ok if its a 2 pole (or handle tied) breaker on a 120/240 3 wire system. probably not ok otherwise. see article 527.

[ October 01, 2004, 11:05 AM: Message edited by: petersonra ]
 
Re: Sharing a neutral

Why would you have to have handle ties? It seems there are (2) seperate gfi receptacles,they are not mounted on the same yoke.

[ October 01, 2004, 11:13 AM: Message edited by: jap2525 ]
 
Re: Sharing a neutral

Originally posted by jap2525:
Why would you have to have handle ties? It seems there are (2) seperate gfi receptacles,they are not mounted on the same yoke.
For temporary circuits, 527.4(E) requires it.
 
Re: Sharing a neutral

can U use a neutral as a switch leg?
If I can, what code supports it?

[ October 04, 2004, 07:29 PM: Message edited by: jrlipse ]
 
Re: Sharing a neutral

Read 404.2(B)

Roger
 