donmore

Member
when sharing a neutral on a 3 phase system do the ckts have to be in order 2,4,6 etc. Or can they be staggered 2,4,12 etc. as long as they are different phases.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: sharing a neutral

As Bob points out, the only concern is ABC.

Any breaker location is irrelevant.

To go into another topic, the grounded conductor if sized for the ungrounded conductors can accommodate any circuits regardless of phase balancing. :D (Don't pay attention to that)

Roger
 