NorthSparky
Member
- Location
- Duluth, MN
I'm looking for where in the NEC specifically it is permitted for 2 phases of a 3 phase panel to share a neutral, and where it says those multiwire branch circuit conductors have to be from separate phases.
I understand they have to be on a 2 pole breaker, or have the handles tied together, and the ungrounded conductors need to be grouped with their associated grounded conductor.
The question has come up because the phase differences in split phase and 3 phase panels. It makes sense on split phase, where they are 180 degrees out of phase that the sum of the neutral currents would always be less than the highest current on one of the conductors, but for a 3 phase panel the phases would only be 120 degrees out of phase. I've seen other posts where they run through the math to show even 120 degrees out of phase they wont exceed the highest current of the most heavily loaded conductor, but just wanted to read it in the NEC for myself that this was permitted. (i.e. to show to the boss)
Thank you for your time.
I understand they have to be on a 2 pole breaker, or have the handles tied together, and the ungrounded conductors need to be grouped with their associated grounded conductor.
The question has come up because the phase differences in split phase and 3 phase panels. It makes sense on split phase, where they are 180 degrees out of phase that the sum of the neutral currents would always be less than the highest current on one of the conductors, but for a 3 phase panel the phases would only be 120 degrees out of phase. I've seen other posts where they run through the math to show even 120 degrees out of phase they wont exceed the highest current of the most heavily loaded conductor, but just wanted to read it in the NEC for myself that this was permitted. (i.e. to show to the boss)
Thank you for your time.