Yesterday I posed a question., about Electrical wiring and Plumbing, etc. sharing a trench. Granted I thought that I had seen something in the code book about not being able to but mixed it up with article 300.8 knowing that that is not the same. But I have some associates that are concerned because this very thing has taken place the feeder wires are tight against the Plumbing pipes. The pipe has need of repair.
I could be wrong, but as I recall water don't mix very well. Now I think it might be a Utility thing about joint use of a trench. Min. of 1' vertical and 2' horizontal separation is required. 300.5(D)(3) warning tape also should be used. I have come to the best of the best for an answer, PLEASE HELP your thoughts or advice would be appreciated. THANKS!!
I could be wrong, but as I recall water don't mix very well. Now I think it might be a Utility thing about joint use of a trench. Min. of 1' vertical and 2' horizontal separation is required. 300.5(D)(3) warning tape also should be used. I have come to the best of the best for an answer, PLEASE HELP your thoughts or advice would be appreciated. THANKS!!