The hospital and nearby clinic share same emergency generator.
The inspector came out and want hospital and clinic must have
their own ATS. Generator's 600A main breaker, 600A feeder, hospital's ATS-E2
and downstream panels (cyan color) have been installed.
The clinic and its panel (yellow color) will be installed. Does anyone see
any code violation with this tap installation to new ATS-E1? ATS-E2 does
not have a protection downstream of 600A CB.
The total emergency load is less than 150kVA. Thanks!
See attached picture.
Thank you.
View attachment SKE.pdf
Thank you.