I will be installing a new service in the area shown on the photo. There are two ground rods installed for the adjacent house. Do I need to drive two more next to the existing or can I share them?
 

Attachments

  • 3003 16th road new meter1.jpg
    3003 16th road new meter1.jpg
    138.7 KB · Views: 2
If you read 250.53, I believe that code requires not only separate ground rods, but that the ground rods be separated by a minimum distance.

If you share the ground rods, then you have the same sort of problem associated with common metallic water piping: neutral current flowing via the shared grounding electrodes and through the neighbor's neutral.

Physics wise, I think it would be preferable to share the ground rods; otherwise currents through the soil could enter one set of ground rods, travel through the neutral wires, and exit the other set of ground rods. But I don't think that is what the code says.

-Jon
 
There are two houses. There is a meter on the rear on one and we will be installing a meter on the side of the other house.
Is what is shown both of those houses? End result being a two family dwelling.

IMO if service disconnects are grouped at one location it kind of doesn't matter if it is considered two structures or not, common grounding electrodes should be fine.

If you only had a single metal water pipe supplying both dwellings - you don't have to install a second metal water pipe just because there is two service disconnecting means.
 
There are two houses. There is a meter on the rear on one and we will be installing a meter on the side of the other house.
They appear very much attached. Are they both on the same property?

And as noted, a single service drop is one service no matter how many service entrance conductors split off of it. The AHJ and POCO may call it separate services if it supplies more than one property.
 
Based on the photo in the OP, this is one structure. 250.58 requires all services, etc. to use the same GES. Installing a SEPARATE GES of, say, 2 more ground rods is not compliant. The OP could add 1 or more ground rods if desired but all electrodes would have to be bonded together to form a single GES.
 
If a multi occupancy building you possibly can have more then one service.

If there is only one service drop or lateral it is still one service though.
 
If you read 250.53, I believe that code requires not only separate ground rods, but that the ground rods be separated by a minimum distance.

If you share the ground rods, then you have the same sort of problem associated with common metallic water piping: neutral current flowing via the shared grounding electrodes and through the neighbor's neutral.

Physics wise, I think it would be preferable to share the ground rods; otherwise currents through the soil could enter one set of ground rods, travel through the neutral wires, and exit the other set of ground rods. But I don't think that is what the code says.

-Jon

Exactly...In Washington we have a state code rule that prohibits sharing ground rods since you will have the bldg. neutrals in parallel and will have objectionable current.
 
Exactly...In Washington we have a state code rule that prohibits sharing ground rods since you will have the bldg. neutrals in parallel and will have objectionable current.
How many older neighborhoods do you have with metal water piping and all services bonded to that water piping?

And the metal shields on telephone, CATV all connected to every service as well?
 
Exactly...In Washington we have a state code rule that prohibits sharing ground rods since you will have the bldg. neutrals in parallel and will have objectionable current.

I thought the Grounding Electrode System was connected through metal water pipe and service neutral so that the entire system was bonded together? That is all structures in the city sharing water pipe and all of the neutrals and ground rods through the system are bonded into one huge system?
 
If you read 250.53, I believe that code requires not only separate ground rods, but that the ground rods be separated by a minimum distance.

If you share the ground rods, then you have the same sort of problem associated with common metallic water piping: neutral current flowing via the shared grounding electrodes and through the neighbor's neutral.

Physics wise, I think it would be preferable to share the ground rods; otherwise currents through the soil could enter one set of ground rods, travel through the neutral wires, and exit the other set of ground rods. But I don't think that is what the code says.

-Jon

I think you are confusing the requirement to have individual electrodes such as ground rods to have a minimum separation of 6' as required in 250.53. This only applies to the INDIVIDUAL ground rods-not the grounding electrode system. All electrodes in a GES must be bonded together.
And as I mentioned in my previous post, 250.58 requires all systems in a building use the same GES.
As for Tom's remarks about Washington State requirements for separate GES for each disconnect, well, I'm not sure what to say about that as it is a direct violation of the NEC.
 
I think you are confusing the requirement to have individual electrodes such as ground rods to have a minimum separation of 6' as required in 250.53. This only applies to the INDIVIDUAL ground rods-not the grounding electrode system. All electrodes in a GES must be bonded together.
And as I mentioned in my previous post, 250.58 requires all systems in a building use the same GES.
As for Tom's remarks about Washington State requirements for separate GES for each disconnect, well, I'm not sure what to say about that as it is a direct violation of the NEC.
IMO there is only one condition which determines one vs. two GES's, and that is whether or not the buildings are on one or two properties.
 