- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
Finally got to do some commercial! It's an office building with a 3 phase 120/208 1200-ish amp service (didn't look, that's a guess) with four meters. Apparently on the rough, some misguided soul pulled a 12-3 run to two furnaces in the attic from panel D, and a 12-3 run to two furnaces on the main floor from panel B. These were supposed to be 4 separate 12-2 runs from each of the four separate panels.
My question (which will focus on one pair): Would it be code-legal (first) and in tune with the laws of physics (secondly) to pull a 12-2 run between panel A and B? In essence, taking power from the A phase of Panel A, and the B phase of panel B, attach it to the existing 12-3 home run, using the neutral from panel B? (Provided I were to test and verify that the phases did match up panel to panel.) The reason being that Tenant "B" doesn't want to pay for the heat for Tenant "A".
Bear in mind: one transformer, one service, 30 minutes labor.
As it was, my idea was controversial, so we spent 8 hours labor getting a new home run to the attic from the main floor. And we ain't done yet. So was I right in my theory, or right in keeping my mouth shut?
--George
My question (which will focus on one pair): Would it be code-legal (first) and in tune with the laws of physics (secondly) to pull a 12-2 run between panel A and B? In essence, taking power from the A phase of Panel A, and the B phase of panel B, attach it to the existing 12-3 home run, using the neutral from panel B? (Provided I were to test and verify that the phases did match up panel to panel.) The reason being that Tenant "B" doesn't want to pay for the heat for Tenant "A".
Bear in mind: one transformer, one service, 30 minutes labor.
As it was, my idea was controversial, so we spent 8 hours labor getting a new home run to the attic from the main floor. And we ain't done yet. So was I right in my theory, or right in keeping my mouth shut?
--George