Thanks Pete,210.4 (2008 NEC) may help you.
Pete
Where a shared neutral is used for combining lighting and other branch circuits, should we use a handle tie between 1-pole breakers to disconnect all ungrounded conductors simultaneously where the wires originate in one junction box?!
thank you
(2) Grounded Single-Phase and 3-Wire dc Circuits. In grounded systems, individual single-pole circuit breakers with identified handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.
I do not see where this section allows what you are saying???
Pete
Read 240.15(B)(1)