Can someone point out the section of the NEC that states each branch circuit needs it's own neutral and can not be shared with another branch circuit.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: sharing of neutral

To be fair, Multiwire branch circuits are kind of prohibited in most hazzardous locations unless a common disconnect means for all ungrounded conductors is used, see 501.18, 502.18, and 505.21 and take note of the exceptions.

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: sharing of neutral

Roger,
I wouldn't go as far as saying that they are prohibited in most classified locations. They are prohibited in Division 1 locations. I believe there are a lot more areas covered by Division 2 rules than by Division 1 rules.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: sharing of neutral

Don, let's change the wording to say 2 out of 3 hazzardous classes. This would be a majority or "most" in this wording. :D

Roger
 