Shed grounding
mobo
MO USA
I have a metal shed I'm going to run electric to. I'm going to install 2 LED overhead strip lights and a duplex receptacle. Other than the equipment ground I'm running with the hot and neutral (grounded conductor) from my house's main panel, should I also drive a ground rod or two at the shed and bond it to the equipment ground?
This sounds suspiciously like a do-it-yourself type question. If you are a do-it-yourselfer we are not allowed to help you perform actual work, but this seems more on the order of a request for information which they sometimes allow from diyers.
The answer to your questions can be found in article 250. The answer will change based on whether you are running a feeder or a branch circuit out to the shed. A feeder would require a grounding electrode system at the shed, while a branch circuit would not. You have not specified which you have.
A moderator may ask you to update your profile with your profession so you might as well go ahead and do so.
Please update your profile with your occupation. The thread will be closed until this is done.