hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have sheet metal shop with 1 arc welder , 1 resistant welder, 1 coil line apparatus
The coil line apparatus assembly drawing show transformer T3030K0023B Acme Transformer link below:
Link of the transformer:
www.hubbell.com
The transformer internal wiring link:
It is wired in reverse has primary as 240/120V delta and secondary 480V delta and its 30kVA. Acme the manufacturer allows it.
The designer is saying the transformer is Not Separately derived, and it came with Coil line apparatus assembly has shop drawings proving transformer came with apparatus and so it is Not part of premise wiring. The transformer does Not need to be grounded per NEC 2014 Section 250.30 since it’s not part of premise wiring. NEC 2014 Section 450 exception no. 2 says NEC 2014 section 450 Not applicable to the transformer.
My questions:
1. NEC 2014 does Not mention for grounding 250.30 or separately derived definition premises served. Does the transformer need to be grounded NEC 2014?
2. Would NEC 2014 section 240.21 apply to this transformer?
3. Would NEC 2014 Section 450.1 exception no. 2 apply with this transformer?
4. Is the transformer separately derived or not?
Low Voltage Distribution Transformer - Three Phase, 480? - 240?120V, 30kVA | T3030K0023B | Acme Electric
My questions: