Came across today a recepticle screwed into a plastic box with sheetrock (general purpose coarse threaded construction screws ) screws, is this legal? I always use 8-32 screws but could this be an alternative?
No, it is not legal because it has not been listed for use in that manner. I suspect the plastic threads have been stripped out and this screw was used to bite into the plastic and make it work. Is it really bad, not in my opinion. Is it wrong, yes.
I found this really neat trick some years back, if you simply "push" the screw in, with some plastic boxes, you only need a couple more turns to tighten it up. Trouble is they wont get very tight after doing that.
I've always wondered if some guys are doing this regularly.
314.27 Exception: A wall-mounted luminaire (fixture) weighing not more than 3 kg (6 lb) shall be permitted to be supported on other boxes or plaster rings that are secured to other boxes, provided the luminaire (fixture) or its supporting yoke is secured to the box with no fewer than two No. 6 or larger screws.
I can't find the 6-32 or 8-32 rule, where can I find that?
I learned many years ago not to use the cheap blue boxes sold at big orange.The problems they cause just are not worth the savings.Perhaps some J B weld then drill and tap it.Or if nobody is looking a 2 inch drywall screw.Really i don't see this causing a problem.
It's a is a mechanical fastener that securely holds the yoke to the box. Absolutely not comming out without the use of a screwdriver. Sits flush to the wall so the plate does not stick out. Poses absolutely no unsafe condition. Corrects a potential hazardous condition.
Hi Gndrod, tooth pick huh. I'm wondering if someone made a 7-32 if that would work on a stripped box. Or 6.5-32
I've never had any problems with the blue boxes. Try to destroy one. I've used that meathod to extract them from walls, not easy. And exept for the 2x3's there not all that cheap. Some of the old work round ones are five bucks.
Allow me to clarify my comment! There is no need to use drywall screws on the new blue boxes.
But when on a service call and I find an old device that one of the 6-32 threads are so stripped that they are no longer fastening Anything, that's when the drywall screws work great. Sorry for the confusion, two very different situations.
It's a simple way to improve a potentially dangerous situation. If using a different type of screw poses a risk of comprimising the integrity of the existing box it should NOT be done. For instance some of those old bake-lite boxes, they will crumble. In that case it wouldn't be an improvement at all.
I use Allied fiberglass boxes, so drywalls are the last option in a situation. An option I'll use, but if you try to use an "8" sized drywall screw in a fiberglass box, it'll blow apart, often times.
Go Broncos! They'll figure it out next year!
(Please...?)
Hey George, I think your fiberglass boxes and the bake-lite boxes I mentioned are very similar composits if not identical. I'm curious as to why you choose to use them. To each their own of course but I'm just curious!
Cut and dried answer is: That's what the shop buys.
We prefer them because if there's a change, they are way easier to eliminate than blue Carlon boxes. They are easier to push wire into than than blue Carlon boxes.
Others would disagree with me, it just preference.