Went to check out situation at a camp the other day. People getting shocked in the showers. We are replacing the service, which is very old and shabby.
I found a bad neutral, 69 volts to phase A and 174 to phase B. No ground wire from the panel feeding bath house. Neutral grounded to ground rods and water main. I think the missing neutral causes the water main to be energized.
Anyone seen similar situations?