Will Wire
Senior Member
- Location
- California: NEC 2020
- Occupation
- Electrical Contractor
I have a customer who's renters complain about getting shocked while taking a shower if they touch the handle or shower head. On this house someone removed the metal piping supplying water service and replaced it with plastic. They have also removed the metal piping under the house and replaced it with plastic. The metal piping still extends up into the walls at the kitchen and bath. The house Electrical Service is grounded with a ground rod. When you test between hot and the metal piping in the shower instead of 120 volts you get 71volts. I am going to bond the isolated metal pipes areas to the service to take care of part of the problem but I was wondering if there has to be a connection between a white wire and ground wire to have the shock at the shower. Any information is greatly appreciated,