Shocking chimney!

Status
Not open for further replies.

JohnJ0906

Senior Member
Location
Baltimore, MD
was sent to a house our company wired today. (different crew)

The GC met me and told me what happened. He had been there Thursday for an unrelated problem, and had noticed a leak in the ceiling. He went up to the roof to check, especially around the chimney, which was close by.

The fireplace is a pre-built model (I call them "mechanical"), wood burner, no gas. Blower underneath, switch controlled.

Chimney is glue-on "stone", rest of house is vinyl siding.

He is checking around the chimney, and gets shocked when he touches the fireplace flue!

Friday he tarps the chimney (still leaking) and gets rapped a few more times even though he is being cautious.

Monday, I get sent there to - get this - "check the building ground"
blink.gif

Luckily, the GC was there to let me in, and I got the story from him direct.



I check the fireplace - every connection tight. No voltage on ground. Check with an extension cord ran to the panel. Climb in the attic and look around the flue- no wires within 3 feet.

Use ampmeter - no current on EGC
OK, I don't like roofs, especially sloped, most especially in the rain. But I gotta find this.

30 volts from the stone mortar to the flue! And 25 to 28 from the shingles to the flue!
Had my helper flip breakers until in went away. It was a bedroom circuit - with no AFCI.
001_huh.gif

The GC then told me that the HO had complained that breaker had tripped occasionally, but only when it rained. So whoever came and "troubleshot" it couldn't find a problem, he took the AFCI off and put a standard breaker on.
censored.gif


Once I knew what circuit it was it took 20 minutes with the trusty megger to find the bad wire, isolate both ends, and bypass it with a piece of romex jumping the 2 receptacles.
Back on roof, check again, no voltage, fish in new wire, replace AFCI breaker.

Evidently, the wire got hit by a siding nail, or a flashing nail. It only became evident when there was rain.

I am furious that someone (who is still employed there - for now) would do something so stupid.


Also, I wanted to share this story, in case someone ever runs into something similar.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You didn't find the nail that was causing the problem? :D Shame on you..:wink:

I remember running an extension cord outdoors and sticking one tester lead in the neutral prong of the cord and using the other tester lead to locate the nail. I would touch every nail head on the siding in the area the fault had occurred until I found it. Of course I had to replace the wire anyway but it was fun finding the sucker.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Dennis Alwon said:
You didn't find the nail that was causing the problem? :D Shame on you..:wink:

I remember running an extension cord outdoors and sticking one tester lead in the neutral prong of the cord and using the other tester lead to locate the nail. I would touch every nail head on the siding in the area the fault had occurred until I found it. Of course I had to replace the wire anyway but it was fun finding the sucker.

2 trips onto a roof in the rain was enough.

Excuse me - MORE than enough.
 

frizbeedog

Senior Member
Location
Oregon
I like troubleshooting stories.

I like troubleshooting stories.

JohnJ0906 said:
I am furious that someone (who is still employed there - for now) would do something so stupid.

Also, I wanted to share this story, in case someone ever runs into something similar.

Thanks for that story.

And who did that guy work for? The one you're furious with. The one who replaced the arc fault breaker.

....and where did you get those animated smiles? Cool. :cool:
 

JohnJ0906

Senior Member
Location
Baltimore, MD
frizbeedog said:
Thanks for that story.

And who did that guy work for? The one you're furious with. The one who replaced the arc fault breaker.

....and where did you get those animated smiles? Cool. :cool:

He works for the same company I do. I don't want to say more about that here.

I originally posted this yesturday on another forum, that has different smilies. A bit of typing, so I copied and pasted from that one to this one.
 

cadpoint

Senior Member
Location
Durham, NC
That is a great story, topped off with a megger, Yes ...
It kind of reminds me of my old computers or anything with an electron flowing through it.
If its going to break it will be in the first hours or days, otherwise its good for it service life. Simplest I know, but so true.
 