Ktmbowhunter
Member
- Location
- United States
Hey there folks....I'm currently trying to bid a shop but there are a few things holding me up. This has a 50' x 75' welding/working area with an additional 25' x 50' office area so the total dimensions are 50' x 100'. There are 3 batrooms complete with EF's, 2 lamp 2 x 2's, and GFCI. The service is a 400A 1ph 240V.
Im using 15-6 lamp T5HO's in the fab area. There are 3 welding outlets, 25 duplex & GFCI's, 1-240V 3Hp compressor, and 3-240V 3/4Hp overhead doors. On the exterior there are 4 LED wallpacks that draw very little. He plans on installing a 31.5kW electric boiler for floor heating.
The office has a kitchen complete with fridge, microwave, and range. None of these I have info on so I figured 12.5kW on the range, 1000W on the microwave, and 800W on the fridge. There are 14-2 lamp T8's that are 1.85A, 3-2 lamp T8's in the bathroom at about an amp a piece, The exhaust fans are 3 amps, and 31 duplex/GFCI's. I have no info on the water heater or the A/C.
I'm concerned that I will be cutting it close after the installation of the A/C and water heater arrive. I'm approximately 200' from the meter. I was planning on going underground with parallel 4/0 THHN. All the help is much appreciated!
Im using 15-6 lamp T5HO's in the fab area. There are 3 welding outlets, 25 duplex & GFCI's, 1-240V 3Hp compressor, and 3-240V 3/4Hp overhead doors. On the exterior there are 4 LED wallpacks that draw very little. He plans on installing a 31.5kW electric boiler for floor heating.
The office has a kitchen complete with fridge, microwave, and range. None of these I have info on so I figured 12.5kW on the range, 1000W on the microwave, and 800W on the fridge. There are 14-2 lamp T8's that are 1.85A, 3-2 lamp T8's in the bathroom at about an amp a piece, The exhaust fans are 3 amps, and 31 duplex/GFCI's. I have no info on the water heater or the A/C.
I'm concerned that I will be cutting it close after the installation of the A/C and water heater arrive. I'm approximately 200' from the meter. I was planning on going underground with parallel 4/0 THHN. All the help is much appreciated!