Saturn_Europa
Senior Member
- Location
- Fishing Industry
- Occupation
- Electrician Limited License NC, QMED Electrician
The boat I work on is connected to shore power using an 400 amp Eaton Breaker. KD3400 breaker with a KT3400T trip unit. The breaker has been tripping at around 250-300 amps. We do not have any short circuits on the boat and the breaker is not tripping when starting large motors. I am pretty sure its tripping on thermal. Last night the breaker tripped, then tripped again shortly after resetting it. When the breaker tripped after being reset, the amperage was right at 250A.
From the trip unit manual:
"Thermal Trip: In accordance with standards requirements the thermal element trips the circuit breaker within 2 hours for an overload of 135 percent and trips inless time for higher over loads. For all currents inexcess of the magnetic setting, the tripping action isinstantaneous. In the overload trip region (up to 5 x lth),the trip current times are the same for AC or DC."
The Line to Line voltage is 480 and 277 to ground. The amps are mostly balanced across the three legs and phase rotation is correct. The breaker is new as of last year. It was replaced because the old breaker was tripping at 250 - 300 amps.
Any ideas on what could be causing this?
From the trip unit manual:
"Thermal Trip: In accordance with standards requirements the thermal element trips the circuit breaker within 2 hours for an overload of 135 percent and trips inless time for higher over loads. For all currents inexcess of the magnetic setting, the tripping action isinstantaneous. In the overload trip region (up to 5 x lth),the trip current times are the same for AC or DC."
The Line to Line voltage is 480 and 277 to ground. The amps are mostly balanced across the three legs and phase rotation is correct. The breaker is new as of last year. It was replaced because the old breaker was tripping at 250 - 300 amps.
Any ideas on what could be causing this?