Hello,
First time posting and I hope you can help!
While excavating we encountered, "BOOM" an existing conduit feeding an existing exterior Shore Power Rack at the edge of the parking lot. Thank God nobody was hurt. The conduit was not indicated on the contract drawings and not properly identified by Dig Safe.
Upon further investigation we discover a rack containing six 100 A fused disconnect switches. Each switch fed a 480 volt Arktite Heavy duty Receptacle for portable trailers. The Rack was fed from an existing pad mount transformer. The transformer also feeds a building with (3) sets of 500 MCM conductors to an MDP in the building .
At some point someone installed an undocumented 3" underground conduit with (6) sets of # 2 CU to a Hand Hole about 50' away from the transformer. They installed (6) 1-1/2 inch conduits underground to the (6) disconnects from the hand hole. The rack is about 15' from the handhole. They pulled a 3 phase circuit to each disconnect switch ( 18 ) conductors Total length of conductors is about 65-70' from the transformer.
When the excavator hit the conduit it damaged the bucket and the conductors were still energized. The transformer was de energized and rack feeders removed. We discovered the fuses at the pole were fine and turned the transformer back on to re feed the Building.
The following discussion started. Was the installation legal ? The Inspector indicated it wasn't because the conductors are un protected and longer than the tap rule allows. Is it a tap ? Did the original installer use the six throws of the hand rule and believe his installation was ok ?
We as the prime electrical contractor are caught in the middle. The Inspector is indicating its not legal. The owners on site electrician says it is. We can not fix and reconnect the feeders because we believe the original installation was not to code.
We site the following :
1) Multiple conductors (6) under one lug is a violation
2) The secondary conductors are not properly protected. The transformer and cut outs were designed for the original building and not the added tapped conductors
3) Parallel conductors are # 2 Minimum would be 1/0
4) Too many current carrying conductors in a conduit. 21-30 conductors would be an ampacity of 58.5 Amps feeding a 100 Amp disconnect switch
We believe the owner must install a Fused disconnect within 10' of the transformer to feed the rack. The feeders to the new fused disconnect/ Shore rack should be increased in size.
Are we correct in holding firm and not re-connecting the existing installation the way it was ? The Inspector is starting to have doubts that he is correct and is indicating he may allow the system to be re - connected as is.
Any help is appreciated.
Vin
First time posting and I hope you can help!
While excavating we encountered, "BOOM" an existing conduit feeding an existing exterior Shore Power Rack at the edge of the parking lot. Thank God nobody was hurt. The conduit was not indicated on the contract drawings and not properly identified by Dig Safe.
Upon further investigation we discover a rack containing six 100 A fused disconnect switches. Each switch fed a 480 volt Arktite Heavy duty Receptacle for portable trailers. The Rack was fed from an existing pad mount transformer. The transformer also feeds a building with (3) sets of 500 MCM conductors to an MDP in the building .
At some point someone installed an undocumented 3" underground conduit with (6) sets of # 2 CU to a Hand Hole about 50' away from the transformer. They installed (6) 1-1/2 inch conduits underground to the (6) disconnects from the hand hole. The rack is about 15' from the handhole. They pulled a 3 phase circuit to each disconnect switch ( 18 ) conductors Total length of conductors is about 65-70' from the transformer.
When the excavator hit the conduit it damaged the bucket and the conductors were still energized. The transformer was de energized and rack feeders removed. We discovered the fuses at the pole were fine and turned the transformer back on to re feed the Building.
The following discussion started. Was the installation legal ? The Inspector indicated it wasn't because the conductors are un protected and longer than the tap rule allows. Is it a tap ? Did the original installer use the six throws of the hand rule and believe his installation was ok ?
We as the prime electrical contractor are caught in the middle. The Inspector is indicating its not legal. The owners on site electrician says it is. We can not fix and reconnect the feeders because we believe the original installation was not to code.
We site the following :
1) Multiple conductors (6) under one lug is a violation
2) The secondary conductors are not properly protected. The transformer and cut outs were designed for the original building and not the added tapped conductors
3) Parallel conductors are # 2 Minimum would be 1/0
4) Too many current carrying conductors in a conduit. 21-30 conductors would be an ampacity of 58.5 Amps feeding a 100 Amp disconnect switch
We believe the owner must install a Fused disconnect within 10' of the transformer to feed the rack. The feeders to the new fused disconnect/ Shore rack should be increased in size.
Are we correct in holding firm and not re-connecting the existing installation the way it was ? The Inspector is starting to have doubts that he is correct and is indicating he may allow the system to be re - connected as is.
Any help is appreciated.
Vin