Hi all,
I think this question has a simple answer... say you have a feeder that's composed, for example, of 3 sets of 3#300 MCM wire (3 phase), protected by a 3 pole, 800 amp breaker.
When you have 600 amps of load current flowing through the feeder, it's 600 amps on each phase (A, B, and C)... however it's 200 amps on each parallel wire, for the total of 600 amps on each phase wire.
If you have a short circuit current of 50,000 amps flowing through the feeder, i'm assuming it flows the same way as normal current? 50k on each phase, but 16,666 amps on each parallel wire... is this correct?
Thanks.