I need to do a short circuit analysis for a new hotel, and all the examples I've seen side step the issue of addressing fully the procedure WITH motors. This includes the Cooper Bussmann pdf book EPR-1, which in Ex. 1 of the problems lists "Motor Contribution*=", and asks you to assume that 50% of the load comes from motors. None of the problem solutions address motor contribution.
So what is the procedure?
At the transformer secondary we add all motor FLA's and multiply by five and add this to the transformer short circuit amps?
How do you account for the X/R ratio? Do you need to?
The comment I got back from the plan reviewer states "... show the calculated short circuit amps at all protective devices downstream from the main protective device and that all protective devices are rated to safely interrupt the available short circuit current."
I wonder what " main protective device" they mean? The switch ahead of the panelboard? The OCPD in the panelboard?
The reviewer listed code section 240-83(c) as requiring this. This seems a stretch when you read that section.
Thanks,
Mike
So what is the procedure?
At the transformer secondary we add all motor FLA's and multiply by five and add this to the transformer short circuit amps?
How do you account for the X/R ratio? Do you need to?
The comment I got back from the plan reviewer states "... show the calculated short circuit amps at all protective devices downstream from the main protective device and that all protective devices are rated to safely interrupt the available short circuit current."
I wonder what " main protective device" they mean? The switch ahead of the panelboard? The OCPD in the panelboard?
The reviewer listed code section 240-83(c) as requiring this. This seems a stretch when you read that section.
Thanks,
Mike