I want to make sure I am doing this short circuit calc correctly so if somebody could review my logic I would appreciate it.
According to the Bussman Plan Reviewers guide for AIC calcs the "Second transformer in a system" calculation goes as followed:
f=Primary side fault current * Primary Voltage * 1.732 (%Z) /100,000 * kVA
M=1/1+f
Secondary side fault current = (Primary Voltage/Secondary Voltage)*M*Primary side fault current.
If I do this math and have 20,345 available fault current at the primary side of the transformer (250kVA) here is what my math returns:
F=20345*480*1.732*7/100,000*250=266395.8
M=1/1+F=3.753
Available fault current = 480/208*3.753*20345=.1762
I find it hard to believe that .1762 is all the available fault current at the secondary side of this transformer, especially when my handy cheat sheet for transformer fault current tells me that a 250kva 208V secondary xfrmr has 36,737 available fault current at the secondary side.
I think I am missing the mark somewhere, any help figuring out where would be greatly appreciated.
According to the Bussman Plan Reviewers guide for AIC calcs the "Second transformer in a system" calculation goes as followed:
f=Primary side fault current * Primary Voltage * 1.732 (%Z) /100,000 * kVA
M=1/1+f
Secondary side fault current = (Primary Voltage/Secondary Voltage)*M*Primary side fault current.
If I do this math and have 20,345 available fault current at the primary side of the transformer (250kVA) here is what my math returns:
F=20345*480*1.732*7/100,000*250=266395.8
M=1/1+F=3.753
Available fault current = 480/208*3.753*20345=.1762
I find it hard to believe that .1762 is all the available fault current at the secondary side of this transformer, especially when my handy cheat sheet for transformer fault current tells me that a 250kva 208V secondary xfrmr has 36,737 available fault current at the secondary side.
I think I am missing the mark somewhere, any help figuring out where would be greatly appreciated.