short circuit calculation & soft loading for Equipment Evaluation

Status
Not open for further replies.

Needhelp850

New member
Location
Norcross, GA
I am doing an arc-flash study. Here is the situation I am coming across and am trying to see how to go by it and understand it.
When analyzing the closed transition scenario (utility parallel to generators), few breakers are failing Equipment Evaluation. However, the client is saying there is soft-loading and the time is limited to 20sec, so not to include this closed transition scenario.

My understanding is that soft loading is for transfer of loads from one source to another. If for 20sec (during soft loading) the system will be in closed transition, I would think we would have to analyze this closed transition scenario for equipment evaluation when doing arc-flash study. Am I correct in saying soft loading will have nothing to do with the short circuit calculation in an event of a fault at 20second or less.
Any suggestions pls..............
 

Ingenieur

Senior Member
Location
Earth
20 sec in parallel sounds wrong
it is usually <10 cycles
irrc the std asco time is 100 ms

for 20 sec both sources must be considered

might help
http://m.csemag.com/index.php?id=95...=79143&cHash=bcab7b43d99a9fa3b6498fd9a9384181

In reviewing the NEC Handbook, Articles 110.9 and 110.10 are a matched pair of requirements. The Code Commentary for Article 110.10 states that “Literature on how to calculate short-circuit currents at each point in any distribution system generally can be obtained by contacting the manufacturers of overcurrent protective devices or by referring to IEEE 141-1993 (R1999): IEEE Recommended Practice for Electrical Power Distribution for Industrial Plants (Red Book).” Furthermore, the Code Commentary for Article 705.1 states that “Article 705 sets forth basic safety requirements for the installation of generators and other types of power production sources that are interconnected and operate in parallel as distributed generation.” Clearly, the use of closed-transition equipment does not equate to distributed generation.
 

publicgood

Senior Member
Location
WI, USA
Ingenieur's quoted article is an often referenced one.

Industry opinion: the NEC leave this as a EOR, AHJ or utility interpretation.

The closed transition is normally restricted to 100ms. If there is a fault, the maximum fault will happen within the first 2-3 cycles. That is under the 100ms.

Some say the chance is unlikely that a fault would happen to be during a closed transition maintenance activity. My response to that is “do you mean during the first time one is done, like during an acceptance test?”

If you have a conversation with all, owner included, and proceed with modeling open transition, document it and distribute to all parties.
 

ron

Senior Member
20 sec in parallel sounds wrong
it is usually <10 cycles
irrc the std asco time is 100 ms

for 20 sec both sources must be considered

For closed transition (make before break), it could be <100ms or for soft loading it could be longer. Depending on the load, it sometimes is 45 - 60 seconds, depending on what the utility will tolerate.

I've found 705.16 (2014) to be more compelling regarding the contribution of both sources during closed transition.

As I mentioned in my first post, if it is my stamp/signature, I add both source contributions together for short circuit calcs (although as I read my first post again, I see I am a bad communicator, but this is what I meant).
 

Ingenieur

Senior Member
Location
Earth
For closed transition (make before break), it could be <100ms or for soft loading it could be longer. Depending on the load, it sometimes is 45 - 60 seconds, depending on what the utility will tolerate.

I've found 705.16 (2014) to be more compelling regarding the contribution of both sources during closed transition.

As I mentioned in my first post, if it is my stamp/signature, I add both source contributions together for short circuit calcs (although as I read my first post again, I see I am a bad communicator, but this is what I meant).

I have spec'ed at least 100 of installs
many for mil sites in AK
many more for water/wasteware/telecom
maybe 1/3 closed trasition
most required 3rd party review
always use largest single source
never had one kicked back in 30 years
it is not meant to operate in parallel
 
Last edited:

ron

Senior Member
I have spec'ed at least 100 of installs
many for mil sites in AK
many more for water/wasteware/telecom
maybe 1/3 closed trasition
most required 3rd party review
always use largest single source
never had one kicked back in 30 years
it is not meant to operate in parallel
Understood. My experience in the data center world is different.
 

Ingenieur

Senior Member
Location
Earth
Understood. My experience in the data center world is different.

I did 2 Mellons (Denver and Pittsburgh) and Progressives in Cleveland (among other data centers)
I currently am involved in an Iron Mountain facility, underground, massive
6 x 2 MW units (they have 2 of these sources)
they only consider the largest source
they have parallel ups and static xfer with over-lap
the engineering firm is one that specializes in data centers/server farms
it comes down to engineering judgement
 

Ingenieur

Senior Member
Location
Earth