Mr. bennie & charlie I will try again ask yhe question about short circuit.
I have 7.5 hp motor connected to MCC at 380 meters. The voltage system is 480V (Line to Line), maximun short circuit at the MCC is 39.55 MVA and i need to calculate the appropriate cable by tree methods, current capacity, voltage drop and short circuit level. I have already calculated this cable and is AWG #4. But i have a doubt, where do i have to calculate the short circuit ? at the motor?s connection or near the MCC.
The motor?s feeder is a continuous (1x3c #4 AWG) by tray and does not hace any connection betwen the ends.
The NEC have some article where define that is necesary the cable calculation by short circuit method?
I have 7.5 hp motor connected to MCC at 380 meters. The voltage system is 480V (Line to Line), maximun short circuit at the MCC is 39.55 MVA and i need to calculate the appropriate cable by tree methods, current capacity, voltage drop and short circuit level. I have already calculated this cable and is AWG #4. But i have a doubt, where do i have to calculate the short circuit ? at the motor?s connection or near the MCC.
The motor?s feeder is a continuous (1x3c #4 AWG) by tray and does not hace any connection betwen the ends.
The NEC have some article where define that is necesary the cable calculation by short circuit method?