I am wondering how anyone calculates short circuit calculations where there is an overhead service and no meter main. Mainly looking at 240/120 single phase. For the first portion (transformer to weatherhead), you need to take the 1.5 times the short current at the transformer for the line to neutral calculation. From the weatherhead to the meter, do you also do this? The reason I ask, is that say you calculate 10,000 at the weatherhead from 15,000 at the transformer. If you do the same calculation from the weatherhead on down, you now get more than 10,000 because this is usually a short run. So once you hit your first point where the wire type changes, would you not use the 1.5 multiplier anymore? This also applies from the meter to the first panel. Where I live, meter mains or service disconnects next to the meter are not very common. Most of the time, the main panel inside is the "service equipment". Just looking for other people's thoughts on this.
Thanks,
Thanks,