We are reviewing a short circuit study and have received some push back on the results. The facility has three (3) MV feeds that step-down to 480V via three (3) 2500kVA transformers. All three of the 480V feeds then terminate in a common switchgear via three (3) 5000A MCBs (the drawings show fused/switches but the shop drawings actually have breakers).
The issue is with the withstand rating of the network protectors, which are close-coupled to the secondary of each transformer. They are only rated for 60kA, but due to all of the feeds terminating in a common switchgear, the fault currents from the other two services flow back into each NP. Therefore, the fault current at each NP basically triples from ~49k to ~145k. The study indicates they fail. We agree with this analysis and the results. However, the manufacturer and the EC believes the study is wrong and that the NPs are actually fine.
My question for this community is do you agree with the results of the study? I have attached an image of the original one-line diagram, as well as a screenshot of the SKM model as well. Any other insight would be greatly appreciated.
The issue is with the withstand rating of the network protectors, which are close-coupled to the secondary of each transformer. They are only rated for 60kA, but due to all of the feeds terminating in a common switchgear, the fault currents from the other two services flow back into each NP. Therefore, the fault current at each NP basically triples from ~49k to ~145k. The study indicates they fail. We agree with this analysis and the results. However, the manufacturer and the EC believes the study is wrong and that the NPs are actually fine.
My question for this community is do you agree with the results of the study? I have attached an image of the original one-line diagram, as well as a screenshot of the SKM model as well. Any other insight would be greatly appreciated.