wirenut1980
Senior Member
- Location
- Plainfield, IN
Hello, I am reviewing electrical calculations as part of a submittal and was wondering if you guys could help me check my math. The submitter identified the available "let-through" short circuit current from a 12,470 V - 480/277 V, 1500 kVA transformer. They are submitting 600 MCM (4 conductors/phase), the length of the run is 50 feet, and they are using a C value of 25,000 per phase. The formula I see in an excel spreadsheet calculator from this site using the point to point method is as follows:
f=(1.732*L*I) / (N*C*E)
M=1 / (1+f)
Available short circuit=I*M
where:
f='f' factor
L=length of conductors
I=available short circuit current from transformer
N=number of conductors per phase
C='C' factor
E=line-neutral, or line to line voltage, which in this case would be 277 V, or 480V
This gives me f=0.0921, M=0.8624, and the available line to line SC current=49,379 Amps. The excel spreadsheet fault current calculator comes up with an answer of f=0.028 for the line to line SC current ?f? factor. My question is, where is this difference coming from between my calculated answer (0.0921) and the one calculated by the spreadsheet (0.028)?
The submitter came up with 51,905 Amps available at the Main Distribution Panel (the next point downstream of the transformer). The formula they used was as follows:
f=(1.73*L*I) / (C*E)
They used E=480 V to get the line to line SC current, C=25,000, and they did take into account the 4 conductors per phase. Their answers were f=0.103189, M=0.906463, and 51,905 Amps available SC current. I understand how they got their answer, but what does the ?C? value represent? I guess all in all it only amounts to a difference of 3,000 or 4,000 short circuit Amps in the end. Sorry for being long-winded. Thanks!
f=(1.732*L*I) / (N*C*E)
M=1 / (1+f)
Available short circuit=I*M
where:
f='f' factor
L=length of conductors
I=available short circuit current from transformer
N=number of conductors per phase
C='C' factor
E=line-neutral, or line to line voltage, which in this case would be 277 V, or 480V
This gives me f=0.0921, M=0.8624, and the available line to line SC current=49,379 Amps. The excel spreadsheet fault current calculator comes up with an answer of f=0.028 for the line to line SC current ?f? factor. My question is, where is this difference coming from between my calculated answer (0.0921) and the one calculated by the spreadsheet (0.028)?
The submitter came up with 51,905 Amps available at the Main Distribution Panel (the next point downstream of the transformer). The formula they used was as follows:
f=(1.73*L*I) / (C*E)
They used E=480 V to get the line to line SC current, C=25,000, and they did take into account the 4 conductors per phase. Their answers were f=0.103189, M=0.906463, and 51,905 Amps available SC current. I understand how they got their answer, but what does the ?C? value represent? I guess all in all it only amounts to a difference of 3,000 or 4,000 short circuit Amps in the end. Sorry for being long-winded. Thanks!