Short circuit current depends heavily on the impedance values of the main utility transformer. In an installation with a short main feeder, the utility transformer may be the only thing between our switchgear and the entire output of hoover dam ending up in a arcing fault in our electrical closet.
I get wildly different values of impedance for utility transformers from different sources. Sometimes I can get this info out of the utility, sometimes I can get part of it. For example, I have used the method outlined in the BUSSMAN EDP-1 HANDBOOK for a long time, as it shows a straightforward method. The old 1984 edition lists impedance of a 300KVA utility transformer as 1.14%R, 4.0%X, 4.16%Z. The newer version online, available here http://www.bussman.com/library/docs/Edp-1.pdf
lists the same transformer as 1.2%Z. The latest utility I called lists their 300KVA transformer as 2.5%Z. With these three numbers, maximum available symmetrical fault current could vary between 8600 and 30,000 amps, according to the quick and dirty calculator available here http://www.bussman.com/apen/software/s_circuit.asp
Is there any consistency in transformer KVA ratings? Does every utility use different transformers?
I get wildly different values of impedance for utility transformers from different sources. Sometimes I can get this info out of the utility, sometimes I can get part of it. For example, I have used the method outlined in the BUSSMAN EDP-1 HANDBOOK for a long time, as it shows a straightforward method. The old 1984 edition lists impedance of a 300KVA utility transformer as 1.14%R, 4.0%X, 4.16%Z. The newer version online, available here http://www.bussman.com/library/docs/Edp-1.pdf
lists the same transformer as 1.2%Z. The latest utility I called lists their 300KVA transformer as 2.5%Z. With these three numbers, maximum available symmetrical fault current could vary between 8600 and 30,000 amps, according to the quick and dirty calculator available here http://www.bussman.com/apen/software/s_circuit.asp
Is there any consistency in transformer KVA ratings? Does every utility use different transformers?