I am performing short circuit calculations and equipment evaluation on a 480V bus with a large amount of induction motor loads that are rated under 50hp. I am using the assumption that the contribution from each motor is 6.5xLRA. The combination of all of these motors results in a significant amount of fault contribution.
The fault contribution combined with the utility contribution cause the need for the UL1558 switchgear which feeds these loads to be rated 85kA. Customer is fighting that the motor contribution should not be included because all of the motors are under 50hp and they want to buy 65kA gear (most likely to save money).
I understand this to be acceptable practice when it comes to arc flash calculations because the inertia is not enough to sustain an arc, but I'm not so sure about low voltage short circuit calculations. Any insight out there would be appreciated!
The fault contribution combined with the utility contribution cause the need for the UL1558 switchgear which feeds these loads to be rated 85kA. Customer is fighting that the motor contribution should not be included because all of the motors are under 50hp and they want to buy 65kA gear (most likely to save money).