When performing short circuit equipment evaluation analysis I've seen study results that either show equipment evaluation based on a "Bus Rating" and others based on "Protective Device ratings" Obviously the intent of the equipment evaluation is to compare the available fault current against the equipment bus rating and rating of protective devices but I curious to see how others convey this information with the various analysis software package.
For the Protective Device rating analysis the software simply lists each protective device and compares their device ratings vs the available fault current. This I guess is the most straightforward way however this can lead to cumbersome results since it will essentially list every protective device (could be 100's) and lead to a quite lengthy results table. Many of these devices will be redundant such a having the same breaker type in a given panel or panels, so you are almost listing all these breakers unnecessarily.
The "Bus Rating" method involves a little more input but seems to provide a cleaner output in my opinion. When modeling a piece of equipment (panelboard, switchboard, etc...) most software programs have fields that can be entered manually for bus rating values such as ampacity, interrupting rating, and X/R value. With this method the bus interrupting rating is based off of the lowest rated device in equipment (as well as taking the bus bracing into consideration) So essentially you look at all the devices in the panel and give the bus an interrupting rating and X/R ratio corresponding to the lowest rated device. For example if there is a panel with all 65kA rated breakers but there is one breaker in the panel rated at 14kA for some reason, then the entire bus rating would be based off of the 14kA breaker rating and its tested X/R value. With this method the output report simply lists each bus and its corresponding value and is much cleaner in my opinion and avoids some of the redundancy with the other method.
I was curious to hear the opinions of others and pros / cons for each method. Is there and instance where the protective device method may be beneficial?
For the Protective Device rating analysis the software simply lists each protective device and compares their device ratings vs the available fault current. This I guess is the most straightforward way however this can lead to cumbersome results since it will essentially list every protective device (could be 100's) and lead to a quite lengthy results table. Many of these devices will be redundant such a having the same breaker type in a given panel or panels, so you are almost listing all these breakers unnecessarily.
The "Bus Rating" method involves a little more input but seems to provide a cleaner output in my opinion. When modeling a piece of equipment (panelboard, switchboard, etc...) most software programs have fields that can be entered manually for bus rating values such as ampacity, interrupting rating, and X/R value. With this method the bus interrupting rating is based off of the lowest rated device in equipment (as well as taking the bus bracing into consideration) So essentially you look at all the devices in the panel and give the bus an interrupting rating and X/R ratio corresponding to the lowest rated device. For example if there is a panel with all 65kA rated breakers but there is one breaker in the panel rated at 14kA for some reason, then the entire bus rating would be based off of the 14kA breaker rating and its tested X/R value. With this method the output report simply lists each bus and its corresponding value and is much cleaner in my opinion and avoids some of the redundancy with the other method.
I was curious to hear the opinions of others and pros / cons for each method. Is there and instance where the protective device method may be beneficial?