That’s data from the customer, not motor manufacturer. Like telling you it is hazardous location, indoor installation, type of grounding, etc. you need the short circuit rating for the starter. AIC of the starter needs to exceed that. Has nothing to do with the motor except that it can affect starting and that it will affect the short circuit rating by contributing to it. That’s all starter data. During the first couple cycles of a fault the magnetic field in the motor core has to go somewhere...it causes a decaying transient on the motor bus until it drains away. The ratings are short circuit, not starting. Can be used for starting calculations though,
You typically get multiple ratings from scenarios. So if I have a generator, I get two scenarios. I might also want one with no motors running (recovery from power outage) and a “normal” load. Main-tie-mains add even more. So usually the power engineer just takes the worst and best cases.