A question about short circuit MVA (MVAsc). If we have a generator of 2 MVA, then what will be its MVAsc ?
A question about short circuit MVA (MVAsc). If we have a generator of 2 MVA, then what will be its MVAsc ?
Thanks. So if a 2 MVA generator has Xd'' = 0.2, then MVAsc = 2/0.2 = 10 MVAsc, this makes sense. I am just being curious that why MVA and MVAsc are not the same. In other words, if the generator is capable to produce 10 MVAsc, then why its useful output power is only 2 MVA (and not 10 MVA)?
Yet another reason is that the running MVA may well be limited by the size of the prime mover (engine or turbine for example), while the rotating mass of the system will allow the MVAsc to be limited only by the generator portion.Thanks. So if a 2 MVA generator has Xd'' = 0.2, then MVAsc = 2/0.2 = 10 MVAsc, this makes sense. I am just being curious that why MVA and MVAsc are not the same. In other words, if the generator is capable to produce 10 MVAsc, then why its useful output power is only 2 MVA (and not 10 MVA)?
generators produce heat and need cooled (air/fan, liquid, gas)
losses (cooling load) = i^2 R
assume rated i = 1 pu
therefore sc i = 10 pu
R is constant
so cooling load is 100 times greater
smoke lol