Could someone let me know it I have this correct please?
If I'm sizing my breaker (Inverse Time Breaker) for a feeder to two single phase motors, I take the FLA of the largest motor and multiply by 2.5 (From Table 430.52). Then add that to the FLA of the second motor and at this point, I choose the next standard size breaker below that value. Is this correct?
If I'm sizing my breaker (Inverse Time Breaker) for a feeder to two single phase motors, I take the FLA of the largest motor and multiply by 2.5 (From Table 430.52). Then add that to the FLA of the second motor and at this point, I choose the next standard size breaker below that value. Is this correct?