If two 50hp, 480 volt soft starters are to be installed in a single enclosure, what does the NEC require in terms of protection of the panel or connected loads?
My thoughts:
Provide a single fused disconnect for both motors and use time delay fuses sized at 125% of the total FLA of both motors with the disconnect switch installed in the enclosure with a through-the-door disconnect handle. Both soft starters being in the same electrical enclosure will be within inches of each other. I am not sure if the wire going from the soft starters will be within 10 feet of the enclosure but if they are I would size the wire for the 125% of the FLA of each motor. If it is greater than 10 feet I would size the wire for the total of the two motors' FLA.
Your comments are welcomed.
My thoughts:
Provide a single fused disconnect for both motors and use time delay fuses sized at 125% of the total FLA of both motors with the disconnect switch installed in the enclosure with a through-the-door disconnect handle. Both soft starters being in the same electrical enclosure will be within inches of each other. I am not sure if the wire going from the soft starters will be within 10 feet of the enclosure but if they are I would size the wire for the 125% of the FLA of each motor. If it is greater than 10 feet I would size the wire for the total of the two motors' FLA.
Your comments are welcomed.