You still haven't really indicated that you know what you are asking about, which makes it a bit difficult to answer.
Assuming you are concerned with the SCCR rating of an overall system; Typically a non-fused disconnect has a very low rating, i.e. 5-10kA, so if you used one in a panel system with those other components, you will drag the overall SCCR rating down to that level. But a fused disconnect will typically be rated at what the fuses are rated for. However the proper way to do this is to look at the AVAILALE fault current and then the LET THROUGH of the fuses to ensure that nothing gets through that exceeds the lowest rated device, in your case 25kA.