I have encounter a problem with a piece of equipment being installed on our site. I have a 480v, 800A MCC. Our short circuit current is calc'd at 19.5 K amps available current. From this MCC I have a bucket with a 50A breaker (65 kaic), #6 XHHW aprox 30' long, feeding a listed 3 phase 480v air compressor. The compressor control cabinet came in listed by CSA (not the US approved version, but that's another story), with a short circuit sticker that said "Equipment is not suitable for use on circuits with more than 5 kaic available". Not being sure, I had the engineer do a calc on the circuit and he came up with 8.3 kaic available. Upon notifacation, the contract had the manufacturer remove the control cabinet for repairs. A month later the unit comes back with the exact same parts in it and a "new" sticker marked "not suitable for use on circuits with more than 100 kaic available". Should I accept this installation? I don't feel the manufacturer made a real effort to make the repairs. As the AHJ inspector, do I reject the entire piece of equipment, regardless of the listing? Thoughts either way????