Hi,
I manufacture control panels. What I have problem with is dealing with panel inspectors, who say that if any component in the panel is rated less than the available fault current, it cannot be certified as a safe installation. The fault current of the panel will be rated according to the weakest component. Irrespective of OCPD - fuse or breaker with higher than available fault current ratings .Their solution is to install an isolation transformer or to source a component which is rated to the available fault current. I have problem to source servo controllers that are rated at 57KA. Installation of transformers is expensive and a waste due to being energized when not in use. Do you have an opinion about this? Thanks in advance for your answers.
I manufacture control panels. What I have problem with is dealing with panel inspectors, who say that if any component in the panel is rated less than the available fault current, it cannot be certified as a safe installation. The fault current of the panel will be rated according to the weakest component. Irrespective of OCPD - fuse or breaker with higher than available fault current ratings .Their solution is to install an isolation transformer or to source a component which is rated to the available fault current. I have problem to source servo controllers that are rated at 57KA. Installation of transformers is expensive and a waste due to being energized when not in use. Do you have an opinion about this? Thanks in advance for your answers.