I'm performing an Arc Flash Analysis for a client and have come across a situation where I have numerous breakers not rated for the available fault current. Previously, the transformer ahead this line-up had failed and it had an impedance of 5.75%. The calculated fault current at that time was around 64.5K. The breakers are rated for 65K. I've heard that breakers shouldn't be used unless the available fault current is less than 90% of the AIC rating of the breaker. What is the rule on this?