Is it possible that an MCC and its components can be series rated with an Upstream feeder breaker similar to a panelbaord?
I know that paneloards and switchboards and their internal breakers can be series rated with an upstream feeder breaker if the combination of breakers is a tested and listed series rated combination documented by the manufacturer. For example 35kA rated breakers in a panelbaord can achieve a higher rating of say 42kA or 50kA if they are series rated with an upstream breaker that is a listed by the manufacturer for achieving this series rating for the downstream breakers.
Is it possible to achieve a similar series rating for an MCC? I am looking at an MCC that is slightly overdutied (42kA rating vs 45ka available fault current) and looking for solutions for getting the MCC to pass the equipment evaluation without having to replace it. Usually with a small overduty situation like this you can simply make the feeder cable longer to bring the fault current down however in this case the MCC is fed with BusDuct so that's not an option?
The MCC in this case is a Siemens MCC with a 42kA rating listed on nameplate and is fed from an upstream CH power circuit breaker. Does anyone know if it is possible to series rate the MCC somehow or have other suggestions for getting MCC to pass evaluation without replacing?
I know that paneloards and switchboards and their internal breakers can be series rated with an upstream feeder breaker if the combination of breakers is a tested and listed series rated combination documented by the manufacturer. For example 35kA rated breakers in a panelbaord can achieve a higher rating of say 42kA or 50kA if they are series rated with an upstream breaker that is a listed by the manufacturer for achieving this series rating for the downstream breakers.
Is it possible to achieve a similar series rating for an MCC? I am looking at an MCC that is slightly overdutied (42kA rating vs 45ka available fault current) and looking for solutions for getting the MCC to pass the equipment evaluation without having to replace it. Usually with a small overduty situation like this you can simply make the feeder cable longer to bring the fault current down however in this case the MCC is fed with BusDuct so that's not an option?
The MCC in this case is a Siemens MCC with a 42kA rating listed on nameplate and is fed from an upstream CH power circuit breaker. Does anyone know if it is possible to series rate the MCC somehow or have other suggestions for getting MCC to pass evaluation without replacing?