If I may, just to clairfy something charlie said, is that the system impedance doesn't change unless you add or subtract loads or equipment, which is true, however I think what needs to be clarified is that at the point in which the impedance is calcualted it will not change. The impedance will be different at every point in the power system and that is why you must re-calculate the impedance at each bus you are interested in analyizing. Hence, computer models. I remember doing hand calcs in college, thank goodness I never have had to resort to them since.
As far as printouts go, it takes an engineer with experience in power system analysis to be able to pick out errors or problems. Otherwise junk input = junk output.
A reactor used for reduced voltage motor starting is related to an autotransformer, where the reactance (inductor) reduces the voltage and thereby reduces inrush current. (The principle of voltage down/current up does not apply during a motor start.) However, torque capability is also decreased, and can be a problem if a lot of starting torque is required.