Hello, I am new to this forum so I hope I am following proper protocol.
I have a new facility that I need to do a short circut calculation for at the main switchboard location.
The following are the specs:
This is a 3-wire, 480 volt, 3 phase installation.
utility transformer size is 750kva with an impedance of 5.4%
utility conductor size from the xfmr to our ct cabinet is 4 paralleled sets of 350kcmil aluminum wire in pvc conduit. Not adequate for this instalation but is utilitys call.
from the ct cabinet to our main switchboard is a buss duct system rated at 2000amp. it is of a double alluminum construction. it is 10' in length with two 90 degree elbows.
our switchboard is rated at 2000 amp and does not have a main breaker. Its buss is rated at 65k. I need a short circuit value for this location. Your help is greatly appericiated. If possiable could you provide something I could print out for posting at the switchboard purposes.
Thank You,
Eric Dutenhoeffer
I have a new facility that I need to do a short circut calculation for at the main switchboard location.
The following are the specs:
This is a 3-wire, 480 volt, 3 phase installation.
utility transformer size is 750kva with an impedance of 5.4%
utility conductor size from the xfmr to our ct cabinet is 4 paralleled sets of 350kcmil aluminum wire in pvc conduit. Not adequate for this instalation but is utilitys call.
from the ct cabinet to our main switchboard is a buss duct system rated at 2000amp. it is of a double alluminum construction. it is 10' in length with two 90 degree elbows.
our switchboard is rated at 2000 amp and does not have a main breaker. Its buss is rated at 65k. I need a short circuit value for this location. Your help is greatly appericiated. If possiable could you provide something I could print out for posting at the switchboard purposes.
Thank You,
Eric Dutenhoeffer