Flex
Senior Member
- Location
- poestenkill ny
I have a situation where #4 ser cable feeds a, lets call it a sub-disconnect, that then feeds 2 240v t-stats with 3400 watts each, 12 guage wire. Also 2 receptacle ckts, 14 gauge wire. And A well pump with 14 guage wire. The sub-disconnect had 60 amp fuses, and is protected by a 2 pole 60a in the main panel. I explain to the homeowner the dangers but unfortunately he has a poor financial status right now. To boot the feed cable is only a 3 wire and is around 90 foot long.
I have a subpanel I can install to him at no cost to safely split everything up, but I'm not interested in changing the feed. However I do have a 140 feet of #6 insulated copper sitting in my shed. If I tye-wrapped the #6 along the existing feed and landed it in the main panel ensuring I keep the neutral and ground apart at the new sub-panel would it be legal.
I dont like to take these kinds of short cuts but this is an elderly lady and I dont mind giving the subpanel and wire considering they were already paid for from other jobs.
I have a subpanel I can install to him at no cost to safely split everything up, but I'm not interested in changing the feed. However I do have a 140 feet of #6 insulated copper sitting in my shed. If I tye-wrapped the #6 along the existing feed and landed it in the main panel ensuring I keep the neutral and ground apart at the new sub-panel would it be legal.
I dont like to take these kinds of short cuts but this is an elderly lady and I dont mind giving the subpanel and wire considering they were already paid for from other jobs.