Question: Okay to use a Jake El inside a wall. (Short Radius Elbow)View attachment 22964

348.42 does not permit it for flexible metal conduit in a covered wall.
350.42 does not permit it for liquidtight flexible metal conduit in a covered wall.
So i'd say no. I don't have time to look for all possible applications.
 
348.42 does not permit it for flexible metal conduit in a covered wall.
350.42 does not permit it for liquidtight flexible metal conduit in a covered wall.
So i'd say no. I don't have time to look for all possible applications.

I would never install one of those concealed, but ... I'm not sure those code sections would not allow it. If we look at the 358.42 section (EMT), it does not disallow it.
 
Is the 'short radius elbow' listed? If not, it can't be used at all, correct?

Edit to add: I see it is listed. So it could be used anywhere a straight coupling could be used, apparently. For EMT, flexible type conduit apparently, but it's not listed for that anyway.
 