When would be short time paralleling (momentary paralleling) required in M-T-M configuration?
Do I need to have synchro check relays in both the Mains and the bus-tie for this?
What are the things I need to consider while doing this?
Closed transition (short time paralleling / momentary paralleling / make before break) is never required, you can always do open transition (break before make).
You would think sync check wouldn’t be required but once in a while somebody makes a mistake and swaps two phases or puts a delta transformer in for wye. Otherwise it is never needed on a basic MTM fed from a common source. Each of the other protective functions mentioned may or may not make sense. I’m a minimalist...the more protective functions you have the more nuisance problems you will have.
I design a lot of critical facilities, and you would be surprised how many decide to go with open transition when they realize the additional cost of the higher short circuit ratings that come along with ~2x fault current.You are right about there not being an installation requirement to have a closed transition system, but there are reliability and serviceability requirements which are usually driven by a customer, design/specification, industry, or continuous industrial process. (Think hospital, data center, emergency systems, etc)
Just a side note, that has nothing to do with the paralleling question. I am seeing a bit of a trend to using a MTTM arrangement. This allows a tie device to be totally deenergized for maintenance, because of the two ties being in series. In a standard MTM arrangement the Tie device always has one side energized which often forces a complete outage for routine maintenance.I design a lot of critical facilities, and you would be surprised how many decide to go with open transition when they realize the additional cost of the higher short circuit ratings that come along with ~2x fault current.
I design a lot of critical facilities, and you would be surprised how many decide to go with open transition when they realize the additional cost of the higher short circuit ratings that come along with ~2x fault current.
Just a side note, that has nothing to do with the paralleling question. I am seeing a bit of a trend to using a MTTM arrangement. This allows a tie device to be totally deenergized for maintenance, because of the two ties being in series. In a standard MTM arrangement the Tie device always has one side energized which often forces a complete outage for routine maintenance.
Only when both mains are on- open one main and open both ties, and the tie closer to the open main is now serviceable.
See post #8. And if you're going to service either main, you have to drop the loads on that bus section; no way around it that I can see. With an MTM setup, how do you service the tie without dropping both buses?
It's all about what you service, when, and what you can afford to shut down to do it. If a complete shutdown is preferred, or at least tolerated, that's one thing (or if you plan on never servicing the gear), but if you need to keep some things running, the design becomes different. Heck, you might have some loads on an transfer switch between bus sections just for this purpose.
My customers will not allow you to work in a cubicle whose only protection from voltage is a set of shutters which can bypassed and manually opened.This is exactly my point. You aren’t really getting anything with an extra tie.
...
Utilize RELT and/or a remote racking mechanism. With shutters in place, service the cubicle. There really isn’t anything you need to do to the bus that would not require a complete outage anyway.
My customers will not allow you to work in a cubicle whose only protection from voltage is a set of shutters which can bypassed and manually opened.
It is not uncommon to use both sides of a MTM lineup to feed the same equipment (for redundancy) rather than supply additional load. Breaker racking and conductor terminations are items with much high probability of failure than transformers and switchgear bussing. I know of several people that think of MTM as a way to have two full rated services, but they forget that total capacity is really limited by the rating of the Tie.
Yes sir, open transition both directions. That is the only way to avoid having to account for the extra fault current in the downstream short circuit equipment rating. Don't get me wrong, I do have clients that have applications that use closed transition, but many are open.So the ATS’s when switching back over to normal from being on emergency are open transition???
And that's kind of it, if the customer wants a higher level of interlocks/lock-outs and is willing to pay for those, why argue? Kind of like scissor lifts, OSHA says you don't need fall protection to work in one, but the site/customer might.My customers will not allow you to work in a cubicle whose only protection from voltage is a set of shutters which can bypassed and manually opened.
It would be easier to do this with a picture, but if you rack out the tie breaker and service it when both main feeders are available, the line and load sides of the tie breaker are not de-energized and can't be serviced. The only way to de-energize the line and load sides of the tie, is to de-energized one of the sources and open the tie for an extended period of time to service that end of the tie, and that would only happen if it were magically not in the same cubicle with the "other" side of the tie that is still energized, which would make the overall task of servicing the tie energized, and not doable in most company's work practice's.1) Why can't I rack out the tie breaker/switch and service it at anytime when both main feeders are available?
2) If both service feeders are available and I can tolerate a "blink", why can't I open a main, close the tie, rack out the open main, and service it at anytime?
3) When both service feeders are available, and both main breakers are closed, wouldn't the open tie breaker/switch have voltage present on both sides of it?