11Haze29
Member
- Location
- Rhode Island
- Occupation
- Electrical Engineer
I have a large residential install which will utilize a pad mount transformer, and a Milbanks 400A meter socket enclosure with a 400A disconnect. Transformer and Meter enclosure will be about 70 feet away from the house. Milbanks tells me the 400A disconnect is actually a circuit breaker with Instantaneous and Long Time. A 400A Square D NQ panelboard will go in the basement of the house. My question to all is this: Since overcurrent protection for the 400A service feeders is provided in the Milbanks meter enclosure - should I install an additional 400A MCB in the NQ panelboard. I'm thinking it is not a mandatory requirement, but it does provide some convenience if you need to 'open' the service MCB. Its a New England location so could be snow on the ground if you need to isolate the service during winter. But a MCB in the panelboard adds cost and increases the height of the panelboard, and how often do you really need to disconnect the whole panelboard from the service. Even with a panelboard MCB, you would still have hot lugs in the panelboard.
What are you thoughts on the subject?
What are you thoughts on the subject?