Should loss of potential be enabled in protective relays? A while back someone told me, and I'm now thinking about it (a lot)- that for a remote end fault (especially on a weak system) the positive sequence voltage at the relay can dip to near zero without an increase in positive or zero sequence current. This would certainly initiate LOP.
The question is, should I set a 120 cycle time delay for LOP? Or just not enable it? What are the consequences of having step distance elements running with a blown fuse or total loss of all 3 phase inputs?
The question is, should I set a 120 cycle time delay for LOP? Or just not enable it? What are the consequences of having step distance elements running with a blown fuse or total loss of all 3 phase inputs?