Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2? I heard it has be a factor of square root of 3
Yes, but the two voltages must be added vectorially, not arithmetically.Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2? I heard it has be a factor of square root of 3
It’s single phase. L1/N and L2/N was 110v. But L1/L2 was 186v. Just trying to understand the calculation behind it.You have to tell us what system is being used? For example single phase 120/240 or 208Y/120?
Well if it is in fact single phase you have a problem.It’s single phase. L1/N and L2/N was 110v. But L1/L2 was 186v.
Are these measured voltages or just numbers from a calculation? If there just from a calculation there is no such thing as 110 volts.It’s single phase. L1/N and L2/N was 110v. But L1/L2 was 186v. Just trying to understand the calculation behind it.
Ok, you are probably reading the high leg of a wye system.I was testing by an equipment. The building is on 3phase but the equipment needed only single.
Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2? I heard its a factor of square root of 3
Well that's a problem. Was that measurement taken at the service? That would be the only way to determine if the utility was providing the proper voltage.We were authorized to test the equipment only. The onsite electricain said that the whole building was receiving 186v.
The square root of 3Where do get 1.73 from?
In a 3Ø Wye system the phase angle is 120°. The 1.73 which is the √3 is derived from that angle.Where do get 1.73 from?