Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2?

dmalkokian

Member
Location
Brooklyn
Occupation
Electrical
Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2? I heard it has be a factor of square root of 3
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Should the voltage of L1/N and L2/N sum to the same voltage as L1/L2? I heard it has be a factor of square root of 3
Yes, but the two voltages must be added vectorially, not arithmetically.

As infinity said, the √3 comes into play with 3-phase systems.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It’s single phase. L1/N and L2/N was 110v. But L1/L2 was 186v. Just trying to understand the calculation behind it.
Are these measured voltages or just numbers from a calculation? If there just from a calculation there is no such thing as 110 volts.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So the building is 3 phase 208Y/120. Phase to phase is 120*1.73. The correct voltages should be 120-N, 208 phase to phase.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I misread your post, you are reading two legs of a wye system.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We were authorized to test the equipment only. The onsite electricain said that the whole building was receiving 186v.
Well that's a problem. Was that measurement taken at the service? That would be the only way to determine if the utility was providing the proper voltage.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
As others have said, the sqrt3 only comes into play if it is two legs of a three phase service you are measuring.
 

dmalkokian

Member
Location
Brooklyn
Occupation
Electrical
Yes the equipment wouldn’t function due to under voltage protection. Was just curious on the calculation of getting 186v between L1/L2
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If there is a 110 - N voltage present you could be seeing around 186.

110 X 1.73 = 190

Have the utility or someone see what is at the service as Infinity said.
 